Title: How is the electrical circuit completed between the powerstation and my home?
Post by: chris on 26/07/2015 21:36:41
We're always told that electricity flows in circuits, but the supplies to houses are from live lines and the neutral lines in the home are grounded to Earth. So how does the current flow back to the power station, does it go through the Earth?
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: PmbPhy on 26/07/2015 21:55:48
We're always told that electricity flows in circuits, but the supplies to houses are from live lines and the neutral lines in the home are grounded to Earth. So how does the current flow back to the power station, does it go through the Earth?
I think you're confused. There are three lines. Two are for power and one is a ground. The ground is the neutral wire that you're thinking about. That's only used when there is a high power device being used like a computer or an air conditioner etc. Didn't you ever wonder why some electrical plugs, like that from an air conditioner, have three prongs? That third prong, the thick round one, goes to ground. However sometimes the term "ground" has a different meaning. It can also mean a common power bus in a DC circuit where the negative wire goes to. That is connected to ground as well.
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: evan_au on 26/07/2015 23:33:42
In remote rural areas of Australia, I have seen electricity distribution using SWER (Single-Wire Earth Return); just one wire is fed to the property at a high voltage, with the current returning via the ground.  At the property, a transformer turns the high voltage into normal residential voltages on a pair of wires (230VAC in Australia vs 2x115V in some other countries). But this SWER system is inefficient, and the supply voltage is poorly regulated; it is a rare exception - it is only done because of the high cost of delivering two wires in remote areas.

In metropolitan areas, you will typically see 4 wires passing down the street. This consists of three phases of "Active", plus a "Neutral". You could imagine the Active carrying current "from" the power grid, and the Neutral carrying the current "back to" the power grid (even though the current flow is symmetrical).

As Tesla noticed, if the load in the street is well-balanced between the three Active phases, there will be no current flowing in the Neutral*. In practice, residential loads are always switching on and off on one phase or another, so the Neutral is often the same diameter as the Active wires.

These 4 wires would be sufficient if we were just interested in delivering electrical power. However, electricity is potentially lethal, so we also have to consider electrical safety. If the supply voltage were "floating", the voltage could rise to thousands of volts in the home, causing insulation breakdown and increasing the chance of electrocution.

This risk may be reduced by connecting one of the supply wires (the Neutral) to an Earth stake at each home or at the transformer (practices can vary, depending on the soil resistivity in each region). This way, the Active voltage won't rise above normal household voltages, and Neutral will be effectively the same as Earth potential. If everything is operating properly, there will be zero current flowing in the Earth stake.

A further safety feature is the "Residual Current Device (https://en.wikipedia.org/wiki/Residual-current_device)", which compares the current flowing in the Active & Neutral wires. If they are not exactly equal and opposite, it suggests that an earthed person may have touched the Active wire, and it cuts off the electricity before a lethal shock is delivered.
 
* You will see that high-voltage transmission towers have a multiple of three wires (if you ignore the top lightning conductor, which is usually thinner). This is possible because high-voltage transformers are arranged to share the current equally between the three Active wires, rendering the Neutral effectively redundant.   
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: alancalverd on 26/07/2015 23:35:11
In the civilised world, all plugs have three prongs except for high power 3-phase plugs which have 5.

Just considering a single phase supply, the incoming cable consists of a "phase" wire whose potential varies at 50 Hz (60 Hz in the far-flung colonies), a "neutral" wire whose potential is very close to zero with respect to earth, and an "earth" wire which is literally pinned to the surface of the planet at various points along the way. The system is designed so that the working current flows between phase and neutral, but all "accessible conductive parts" (ACPs) of any machine (i.e. metal casings, screws etc) are connected to earth.

The reason for this complication is that the high voltage generating and transmission system produces 3 alternating voltages with a 120 degree phase difference between any pair, and the local mains voltage distribution network is established so that the current demand in each phase is pretty well balanced. If the phase currents are perfectly balanced there is no net return current along the transmission line neutral. You can thus eliminate the neutral conductor and send "bulk" electricity through 3 wires instead of 6, halving the infrastructrure cost.

However as we get closer to the consumer the phase currents will become less balanced as different consumers switch on various appliances, so there will be some net return current and you need a neutral conductor. Since the neutral conductor will have a finite impedance, its potential at the consumer end will not always be zero, so we provide an additional "protective earth conductor" (PEC) that normally carries no current: its function is to ground the ACPs so that any fault that would otherwise make the casing live, simply blows the protective fuses or trips.     

You can get away without a PEC if the consumer device is "double insulated", i.e. constructed so there is no possibility of anyone coming into contact with the live or neutral. 
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: Colin2B on 26/07/2015 23:51:24
We're always told that electricity flows in circuits, but the supplies to houses are from live lines and the neutral lines in the home are grounded to Earth. So how does the current flow back to the power station, does it go through the Earth?
I think you are in UK. PmbPhy is answering with US system which I believe provides 110v for low wattage appliances and 220v for higher.
In UK we have 230v supplied on 2wires Line (L, brown) and Neutral (N, blue). The L wire is what most people would consider to be the live part carrying power into the appliances, the N is the return path to the supply system. Earthing arrangements depend on your particular installation and can be one of 5 types, some of which are pretty well obsolete. This can be confusing as the most common system for new housing combines N and E in a single conductor which is separated out at the supply box/meter. Because of the resistance of the supply cable it is possible for the N wire to rise above 0 so other protective measures are provided including bonding the earth wire to metalwork eg pipes to prevent dangerous voltages in the case of a fault. Further confusion is due to older systems where there was an earth connection to a plate in the ground, this was never intended as a return path for the current.
Because the current in the L and N wires is the same there are devices which detect any imbalance (RCD - Residual Current Device) due to a fault and disconnect the supply. Such an imbalance could be a fault causing current to flow to earth or someone touching the circuit and again causing current to flow to earth.

Edit: just noticed that Alan C has replied while I was typing, his is a more complete answer than my top level summary.
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: chris on 27/07/2015 08:21:10
Thank you for the comprehensive answers everyone.

But I do not follow Tesla's observation "...if the load in the street is well-balanced between the three Active phases, there will be no current flowing in the Neutral."

Can you please explain how this comes about?
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: Colin2B on 27/07/2015 09:18:14
..if the load in the street is well-balanced between the three Active phases, there will be no current flowing in the Neutral."

Can you please explain how this comes about?
The 3 phases are 120° apart so if they are equal the sum is zero (think of it as a vector sum with 3 vectors 120 apart). The loads would have to be carefully balanced as any inductive load would give an additional phase shift.
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: alancalverd on 27/07/2015 10:15:01
This accounts for the difference between the high and low domestic mains voltage in the USA: the voltage between live phases is  nominally 208V rms, but each phase is nominally 110V to the common neutral. There is a higher voltage industrial standard in the USA giving 480/277 volts.

In Europe the single standard is generally 400/230V. It is common for all three phases to be delivered to domestic users in parts of Germany and Scandinavia as this makes the supply to and balancing of large fixed domestic loads such as cookers and washing machines a lot easier, but ordinary plug sockets all run on one phase per house and you need a professional to install your fixed appliances (if you swap two phases, all the motors run backwards!)
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: Bored chemist on 27/07/2015 10:34:21
Even if the loads are not well balanced it's cheaper to have a single neutral wire the same gauge as the live phases than to have 3 return wires that gauge.
Much of the "return" current rns up and down that wire between users, rather than back to the power station.
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: evan_au on 27/07/2015 10:45:57
Quote
Tesla's observation "...if the load in the street is well-balanced between the three Active phases, there will be no current flowing in the Neutral."
Can you please explain how this comes about?

Tesla invented the three-phase AC electrical distribution system, competing with Edison's more established DC electrical distribution system.

The AC system has three Active wires, each carrying a sine wave with the same amplitude of AC voltage (eg 230V rms = 325V peak) at the same frequency, but with a phase that is separated by 120°. Plus the Neutral wire, which is close to the Earth voltage (lets call it 0V; in practice it should be < 1V for safety reasons).

The voltage on the three Active wires keeps chasing after each other - a pattern that is extremely useful if you want to power an electric motor, as the magnetic field from 3 coils continually sweeps out a circle, spinning the machine's rotor.

Lets call the phases black, red and blue. So if the black phase is +325V relative to Neutral at some instant in time, the  blue and red phases will have a voltage of half this amplitude, but negative, or -162V. So even though all the voltages are continually changing, the sum of the voltages at the Neutral wire is always zero if the loads are balanced.

With a resistive, capacitive or inductive load, the currents in the three wires will also be sine waves, with a 120° phase difference. Similar logic applies so that if the current is 100A in each wire, the sum of the currents in the Neutral wire is always zero, even though the currents in each Active wire are always changing.

Electrical engineers describe the 3-phase electrical supply  (https://en.wikipedia.org/wiki/Three-phase_electric_power)with a phasor diagram (https://en.wikipedia.org/wiki/Phasor): the three radiating arrows represent voltages or currents with the same amplitude and frequency, but a 120° phase difference. The time-based oscilloscope trace of three sine waves is an equivalent representation that may be familiar to more people.
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: alancalverd on 27/07/2015 12:26:28
The more I learn about Tesla, the more I recognise him as a genius - as well as a naive fool! If he hadn't come up with 3-phase AC supplies, I wonder what state the whole of industry would be in today?
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: chris on 29/07/2015 08:08:53
Thanks everyone for patiently explaining this. But can you provide clarification on one aspect of the points above:

The zero in the neutral line, is that relative to the powerstation, or the local substation and Earth?
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: Colin2B on 29/07/2015 10:20:02
The zero in the neutral line, is that relative to the powerstation, or the local substation and Earth?
It is relative to itself.
The neutral conductor is the zero reference point, whether it is connected to earth or not, and all the line phase voltages are measured relative to that neutral.
In addition the neutral is connected to earth at various point for safety eg generator, substation, consumer exact arrangement depend on the country and supply system. So at those connection points neutral and earth would have the same zero voltage.
However, when you say "The zero in the neutral line" are you talking about the current? This is not measured by taking a reference point. Because current flows in/through a wire we can measure it in a number of ways:
- measuring the voltage drop across the load and using the known impedance of the load to calculate the current
- putting a sensor in the line - low resistance, coil etc and using that to drive a meter
- measuring the magnetic field around the wire eg clamp meter.
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: evan_au on 29/07/2015 12:33:18
The electrical transmission between your home and the power station is built in several fairly independent segments, with transformers in between (yet another advantage of Tesla's 3-phase AC power system!). The decision about whether to have a Neutral wire or not, and where to earth it can be made on a segment-by-segment basis.

The first segment is between the power station and a high voltage substation; this segment may run at a voltage like 250kV-750kV AC, and the high voltage means low current, so the power can travel for hundreds of km with little loss. The current and voltage is very well balanced here.
In high voltage transmission systems, the transformer wires are sometimes connected in a "Δ" (Delta) configuration (https://en.wikipedia.org/wiki/Three-phase_electric_power#Three-wire_and_four-wire_circuits). You can't measure the voltage at the neutral wire, or measure the current in the neutral wire, because there isn't a place to connect a neutral wire!

After several more segments, at successively lower voltages (each of which are designed to balance the current between phases)...

The last segment is between your home and a transformer in the street, converting 11kV to 230V or 110V to supply household appliances. Because the voltage is so low, the current is high, and the losses are high, so this segment is kept as short as possible. The voltage is fairly well balanced between phases.
It is this last segment which comes closest to the public, so safety is most critical for this segment. The street transformer has a "Y" (Wye) configuration (https://en.wikipedia.org/wiki/Three-phase_electric_power#Three-wire_and_four-wire_circuits), with a central point to connect a Neutral wire. This central point is also attached to earth at the transformer.

If we measure voltages relative to the earth stake at the street transformer:
Normally, there is not a continuous neutral connection all the way from home to power station (which could be hundreds of km away). The reason is that a Coronal Mass Ejection from the Sun can induce high voltages in the body of the Earth, causing very high currents in the neutral wire. The frequency of these voltages is very low, and this can cause transformer overload and breakdown, such as happened in Quebec in 1989 (https://en.wikipedia.org/wiki/March_1989_geomagnetic_storm#Quebec_blackout).

In the absence of magnetic field disturbances or power line faults, there should be

Sorry about the essay...
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: chris on 29/07/2015 14:35:58
Thanks, again. This is turning into such a fascinating and educational discussion for me!

If I may, then: at the first step down between power station and downstream grid, where the neutral line is omitted, is the "neutral" side of the transformer winding connected to the other two supply phases so that, as you highlighted above, these act as the sink for the current when the input line is "high"; in turn, this line is the sink for the inputs from the other phases then they are high?

Chris
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: scotty stull on 29/07/2015 16:30:21
Most portable generators are not neutral bonded, meaning that the ground is not connected to the neutral side of the generators out put windings. Notice i said "windings" were two coils are connected electrically, this is the neutral bond. If a power line that is hot falls to the ground it will create a conduction path through the ground-neutral connection back to the H. V. transformer.
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: Colin2B on 29/07/2015 19:18:00
If I may, then: at the first step down between power station and downstream grid, where the neutral line is omitted, is the "neutral" side of the transformer winding connected to the other two supply phases so that, as you highlighted above, these act as the sink for the current when the input line is "high"; in turn, this line is the sink for the inputs from the other phases then they are high?

Chris
I might be misunderstanding your question so a somewhat long-winded answer.
On the downstream side the transformer is wired delta and there is no neutral connection. Each of the 3 transformer secondary windings are connected together in a triangle and the phase of the windings arranged so that line end of one winding acts as the reference (or neutral if you want to think of it that way) for the next, so around the triangle. The transmission system is then 3 wire with one connection to each of the points of the triangle. So across any of the windings the 2 connections effectively run as an output and a neutral, or sink, for one phase. So each of the connections are indeed fulfilling 2 functions at the same time.
Does that make sense, or have I completely misunderstood your question?
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: chris on 29/07/2015 20:42:16
No, Colin, that is EXACTLY what I was asking and your answer was spot on!

So, the "neutral" from my house to the substation is actually an Earthed line connected to one of the other two incoming phases (ie one of the other two points on the triangle as you put it)?

Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: scotty stull on 29/07/2015 21:28:31
Wye windings is the more common set up , the neutral is connected to the center tap of all three legs which makes for a perfectly symmetrical load balance. Some wind generators have both a wye and delta winding,  when the wind is weak electronics will switch to the delta windings. Delta windings generate to much voltage when the wind is to strong.
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: syhprum on 29/07/2015 22:44:03
When I first encountered it I found the USA system rather confusing they use a delta three phase system with one output winding centre tapped and grounded to supply either 117 or 234 volts for domestic use.
the result is if you check the voltage of the delta lines relative to ground you find two of 117v and one of about 160v which rather puzzled me !
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: Colin2B on 29/07/2015 22:52:15
No, Colin, that is EXACTLY what I was asking and your answer was spot on!

So, the "neutral" from my house to the substation is actually an Earthed line connected to one of the other two incoming phases (ie one of the other two points on the triangle as you put it)?
I had assumed you meant the first step down from generator to grid. You are meaning the consumer end.
The delta system is only used for transmission between the intermediate transformers. In the grid system. So in the UK the generators are outputting Star or Y configuration into the transformer to be converted to delta for long distance transmission (where the currents can be better balanced) and then back to star for local service. So your neutral goes back to the centre tap of the star/Y.
Your most likely earth arrangement, unless your property is very old, will be what is called Protective Multiple Earthing (coded TN-C-S) where the earth from your nearest transformer is carried on the neutral conductor to your home.
It can seem quite complicated, but I think we are there.


Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: evan_au on 29/07/2015 23:15:35
Quote from: Chris
So, the "neutral" from my house to the substation is actually an Earthed line connected to one of the other two incoming phases (ie one of the other two points on the triangle as you put it)?
In 230V countries*, for safety reasons, residential street supplies use a "Y" substation configuration, with an Earthed neutral.
 [ Invalid Attachment ]
If all houses on the street just had 3-phase appliances, the current and voltage would be balanced in all 3 phases (red, blue, black). No current flows in the neutral or the earth, because all 3 currents cancel each other.

If a house has a 1-phase appliance (and all do), it draws current from just 1 phase (red, in this example). The current returns to the substation via the neutral wire. Almost no current flows in the earth wire.

Houses in the street are wired so that different single-phase houses are connected to different phases, so although the neutral currents may not cancel within the house, they are mostly cancelled in the street neutral (because the neutral current from one house is partially cancelled by the neutral current from the adjacent houses, on a different phase).

The street transformer side facing the power station generator may be wired in a Delta configuration, as this shares the unequal currents on the subscriber side more equally across the three phases. But this side can have no Earth connection. An Earth connection for this segment could be provided at the next substation, if it were wired as a Wye.

*110V countries have some different arrangements, one of which  (https://en.wikipedia.org/wiki/File:High_leg_delta_transformer.svg)sounds like what Chris & Syphrum describe.
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: chris on 30/07/2015 08:56:00
Thanks everyone; I have learned so much from this discussion. While I had a notion of what was going on previously, now I actually understand properly how it works.

This interaction has made me think that, if only we had more resources, we could set up a system for summarising the salient points of relevant or resolved threads to produce a distilled, high-quality synopsis. Maybe something to think about...

Many thanks all...
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: syhprum on 30/07/2015 10:29:10
When servicing TV,s many years ago I found in one house the line voltage had dropped to about 130 volts and varying wildly which I diagnosed as a disconnection between the neutral connection of the local distribution transformer and the neutral line.
connecting the neutral line to ground at the house made a temporary fix so that I could check the TV
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: evan_au on 02/08/2015 05:31:16
Two applications where the return path really did occur through the body of the Earth:
In both of these applications, the voltages and currents are far less than those involved in today's household power supplies, and don't create a health risk to those walking near the earth stake. But high-resistance rocks (eg granite) can make it harder to get a good circuit.
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: alancalverd on 02/08/2015 14:54:43
There was an interesting incident a few years ago where the insulation of an underground  phase line was damaged. This set up a potential gradient to the nearby earthing point of the neutral line, such that the voltage drop across a few centimeters of fairly dry soil was too small for barefoot humans to detect, but across a couple of meters was enough to kill a horse. Which it did, twice, IIRC.
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: wolfekeeper on 03/09/2015 18:21:19
Interestingly the reason we have earths on the neutral is mostly for electrostatic reasons:

http://amasci.com/amateur/whygnd.html

If you don't have it, it will work fine nearly always, but occasionally you'll get huge sparks jumping out of equipment at you, because the L/N system (which is isolated) will have floated up to some high voltage relative to earth, and you're often connected to earth... zap!
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: syhprum on 16/05/2016 10:49:31
American homes are normally supplied with single phase 220v with a grounded centre tap to supply low power devices with 110v.
What is the KVA rating of the local transformers and how many homes does it supply or does each home have its own transformer ? 
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: jerrygg38 on 14/07/2016 14:15:51
I spent 5 years working for Con Edison in NY Distribution Engineering Dept. We had three phase "Y" systems for the low voltage end 120/208 volts. This had a common ground. We had 3 phase delta 13,200 volt systems which did not a common ground where current flowed. the lead cables were externally grounded to the ground for safety. When they worked on them they would spear them to make sure they were switched off. Sometimes we found private contractors trying to work them alive and we shut them down.
We had two phase systems where the power had 90 degree differences. For street lights we had an isolated series constant current circuit. Sadly during storms if the voltage at the break point would rise to 5000 volts and linemen picking up the normally safe wires would be killed. Thus the old constant current circuits can be dangerous. We also had DC circuits to homes (worked 1956-1961) slowly the homes were converted to AC and Con Ed would supply the people with new fans. We also provided substations for the DC subway lines. (About 500 volts DC- don't touch the third rail) Most country/ surburban areas have 120/240 volts in their local transformer to their house. In any event the advantage of the delta system is there is only three wires needed for the transmission but you must put in ground rods by the transformers for safety.
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: jerrygg38 on 14/07/2016 14:22:09
Another interesting thing at con Edison was power to industrial welding companies. The spikes are brutal and they use series capacitors for the power line. Normally parallel capacitors help to keep spikes down but we had a least one company that needed the series capacitor circuit.
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: evan_au on 15/07/2016 10:19:40
Quote
how many homes does it supply or does each home have its own transformer?

I recently saw the following arrangement in Canada (which tends to follow US practice in many areas).
- The high-voltage wires are the 3 wires at the top of the pole.
- There is a single-phase transformer attached to each high-voltage wire, each producing single-phase "low" voltage.
- The 3 phases of low voltage are fed into a single large building (to the left), and also along the street to several houses (to the right).

I didn't look closely enough to see if there was a kVA rating stamped on the transformers.

In Australia, we tend to use three-phase transformers in suburban areas. Just as a "Delta" wiring system does not need an Earth (the currents in the three phases almost cancel), the magnetic flux in a three-phase transformer almost cancels, and you can use less iron overall than in three single-phase transformers.
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: William McC on 21/08/2016 14:41:18
No, Colin, that is EXACTLY what I was asking and your answer was spot on!

So, the "neutral" from my house to the substation is actually an Earthed line connected to one of the other two incoming phases (ie one of the other two points on the triangle as you put it)?
I had assumed you meant the first step down from generator to grid. You are meaning the consumer end.
The delta system is only used for transmission between the intermediate transformers. In the grid system. So in the UK the generators are outputting Star or Y configuration into the transformer to be converted to delta for long distance transmission (where the currents can be better balanced) and then back to star for local service. So your neutral goes back to the centre tap of the star/Y.
Your most likely earth arrangement, unless your property is very old, will be what is called Protective Multiple Earthing (coded TN-C-S) where the earth from your nearest transformer is carried on the neutral conductor to your home.
It can seem quite complicated, but I think we are there.

Some areas have the "high leg" other areas have balanced three phase. NYC still has balanced three phase, at least the last time I put a four channel scope to it at work, about a year ago. Some NYC buildings suffer from neutral to ground differentials as high as 24 volts though. That is reaching control voltage levels.

Out on the Island, Long Island some places still have balanced 208 other places have the 230 high leg.

When running 110 volt circuits you have to be careful which breaker (which leg) you hook up to, in the three phase box, that has a high leg, or you will get a surprise when you run your 110 volt equipment off that leg. I have seen voltages to ground from the high leg as high as 195 volts. In the panel there are usually two rows of breakers, the breakers run from top to bottom, alternating Line 1, Line 2, Line 3. If line 2 is the high leg usually marked by a piece of red electrical tape, sometimes blue tape, it will output high voltage to neutral and ground. Years ago different authorities claimed different color coding. Some authorities claimed black and red were standard color coding for single phase 220. Others claimed that blue and black were the standard color coding for 220 volt systems. It pays to check voltage to neutral and ground to make sure. I have worked on both color coded systems many times.

About ten years ago we had "RMS" (Root Mean Square) meters. But they were not "True RMS" meters. Haha. When we would hook up large Roof Top AC units, we of course check the power and we would read 217 to 219 volts. But in actuality that was 208 power. An analog meter would read much higher voltages. Balanced 208 reads 208 from my experience.

The primary taps on the low voltage control board transformer were usually set to 220-230 volts form the factory. But when we would fire up the unit, we would get a buzzing out of the 24 volt relay powered by the lower voltage transformer. It worked but was obviously not correct. The fix was to hook the 208 primary tap of the low voltage transformer up to the line voltage, which was actually 208 volts. The fans and compressors ran on either 208 or 230.

Today even with a Fluke True RMS meter, I see voltages over 240 volts from single phase 230 which used to be 220. Most equipment has a maximum voltage rating of 243 volts. In the same area 125 volts was coming from the 110 volt outlets. Which we now expect to see 120 volts from the 110 volt outlets.

It is funny but the old Simpson analog meters, when used on true balanced three phase AC, that is sometimes installed for gas stations to prevent an accidental high voltage leg from powering gas pumping equipment, read 110 volts from 110 volt outlets. Yet the same analog Simpson meter reads 145 volts from a high leg systems 110 volt receptacle. That is why guys stopped using the Simpson meters.

Things change a lot.

Sincerely,

William McCormick







Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: David Reichard on 15/09/2016 04:35:05
I have seen a published engineer's study of ground current strengths or voltages actually measured in Columbus,Ohio circa the turn of the 19th century.I don't know if AC or DC.I think the publication was in the Columbus Metropolitan Library's main branch.The actual physical earth ground is a very large collection of parallel return conduction paths which enmasse would have a low resistance,even though any one of them might not have a low resistance.That is because all the small currents they carry can add up to quite a large current.It's complicated with AC because of capacitive and inductive effects.(phase)
Title: Re: How is the electrical circuit completed between the powerstation and my home?
Post by: William McC on 17/09/2016 02:18:52
I have seen a published engineer's study of ground current strengths or voltages actually measured in Columbus,Ohio circa the turn of the 19th century.I don't know if AC or DC.I think the publication was in the Columbus Metropolitan Library's main branch.The actual physical earth ground is a very large collection of parallel return conduction paths which enmasse would have a low resistance,even though any one of them might not have a low resistance.That is because all the small currents they carry can add up to quite a large current.It's complicated with AC because of capacitive and inductive effects.(phase)

www.youtube.com/watch?v=pFtoqm3ELLI

It is all about capacitors. The surface area, of a conductor connected to ground is very important. If you have ever welded on your back, while you are wet, you know for sure that cement conducts 40 volts of DC current very well. The formula for a capacitor uses three inputs the ohms or resistance of the dielectric, the thickness of the dielectric and the surface area of the dielectric connected to the conductor. As a welder, electrician, plumber, and server room tech as well as many other fields, you always have to keep in mind which part of the capacitor you are at any given time. There are air capacitors condensers, that you can become part of very easily.

Sincerely,

William McCormick