  4. Does the primary winding of a power substation step down transformer need ground
« previous next »
  • Print
Pages: [1]   Go Down

Does the primary winding of a power substation step down transformer need ground

  • 9 Replies
  • 988 Views
  • 3 Tags

0 Members and 1 Guest are viewing this topic.

Offline theThinker (OP)

  • Sr. Member
  • ****
  • 106
  • Activity:
    0%
  • Thanked: 1 times
    • View Profile
Does the primary winding of a power substation step down transformer need ground
« on: 14/12/2021 08:05:18 »
I assume the single phase substation taps power from one of the 3-phase transmission line. One terminal of the primary connects to the transmission line. Does the other terminal need to be earthed ?

Logged
 



Offline Bored chemist

  • Naked Science Forum GOD!
  • *******
  • 27196
  • Activity:
    100%
  • Thanked: 909 times
    • View Profile
Re: Does the primary winding of a power substation step down transformer need ground
« Reply #1 on: 14/12/2021 08:47:41 »
No, but it's safer that way, and easier in practice.
The single phase 230 volt power delivered to my house is actually one line from a 3 phase system. My neighbours are on the other two phases.
Light industry is supplied with all 3 phases via the same system.
Logged
Please disregard all previous signatures.
 

Offline theThinker (OP)

  • Sr. Member
  • ****
  • 106
  • Activity:
    0%
  • Thanked: 1 times
    • View Profile
Re: Does the primary winding of a power substation step down transformer need ground
« Reply #2 on: 14/12/2021 14:45:43 »
Thanks.

I have just read a little about Wye Delta connection and have a slightly better understanding. 
Logged
 

Offline theThinker (OP)

  • Sr. Member
  • ****
  • 106
  • Activity:
    0%
  • Thanked: 1 times
    • View Profile
Re: Does the primary winding of a power substation step down transformer need ground
« Reply #3 on: 14/12/2021 15:44:51 »
Some related questions:
1) Assume the power station generator is Y connected. Can the neutral point be earthed?
( I think it would be a "fault" condition).
2) Assume we take out the iron core in the step-up transformer - 30kV to 300kV. If we try to run the system with this air core, what will happen?
Logged
 

Offline vhfpmr

  • Sr. Member
  • ****
  • 416
  • Activity:
    1.5%
  • Thanked: 27 times
    • View Profile
Re: Does the primary winding of a power substation step down transformer need ground
« Reply #4 on: 14/12/2021 17:24:58 »
Quote from: theThinker on 14/12/2021 15:44:51
Some related questions:
1) Assume the power station generator is Y connected. Can the neutral point be earthed?
( I think it would be a "fault" condition).
It's not a fault, an earthed system needs to be star connected so that the star point provides a common earth for all phases. In a delta system you'd have to earth one of the lines, in which case you'd end up with one phase live at both ends.
Quote
2) Assume we take out the iron core in the step-up transformer - 30kV to 300kV. If we try to run the system with this air core, what will happen?
The magnetising current will go though the roof because you've lost most of your inductance, and the leakage inductance will go up because you're losing a lot of your coupling.
Logged
 



Offline Bored chemist

  • Naked Science Forum GOD!
  • *******
  • 27196
  • Activity:
    100%
  • Thanked: 909 times
    • View Profile
Re: Does the primary winding of a power substation step down transformer need ground
« Reply #5 on: 14/12/2021 17:26:01 »
Quote from: theThinker on 14/12/2021 15:44:51
Can the neutral point be earthed?
Yes
https://en.wikipedia.org/wiki/Three-phase_electric_power#/media/File:3_Phase_Power_Connected_to_Wye_Load.svg
Quote from: theThinker on 14/12/2021 15:44:51
If we try to run the system with this air core, what will happen?
Something will fail. If you are lucky, it will be a fuse.
Logged
Please disregard all previous signatures.
 

Offline theThinker (OP)

  • Sr. Member
  • ****
  • 106
  • Activity:
    0%
  • Thanked: 1 times
    • View Profile
Re: Does the primary winding of a power substation step down transformer need ground
« Reply #6 on: 15/12/2021 04:38:25 »
Quote from: vhfpmr on 14/12/2021 17:24:58
Quote from: theThinker on 14/12/2021 15:44:51
Some related questions:
1) Assume the power station generator is Y connected. Can the neutral point be earthed?
( I think it would be a "fault" condition).
It's not a fault, an earthed system needs to be star connected so that the star point provides a common earth for all phases. In a delta system you'd have to earth one of the lines, in which case you'd end up with one phase live at both ends.
Quote
2) Assume we take out the iron core in the step-up transformer - 30kV to 300kV. If we try to run the system with this air core, what will happen?
The magnetising current will go though the roof because you've lost most of your inductance, and the leakage inductance will go up because you're losing a lot of your coupling.
1) I don't understand. It seems connecting the neutral to earth is like a short circuit. When the generator runs, current will leak, supplying to earth.  Even without the earth, the generator will still work. The neutral is at 0 potential, but a "zero" is only relative to all the line voltages and should be OK.
2) I think correct. With nearly no inductance, the stator coil may even explode. 

Logged
 

Offline Bored chemist

  • Naked Science Forum GOD!
  • *******
  • 27196
  • Activity:
    100%
  • Thanked: 909 times
    • View Profile
Re: Does the primary winding of a power substation step down transformer need ground
« Reply #7 on: 15/12/2021 08:42:26 »
Quote from: theThinker on 15/12/2021 04:38:25
When the generator runs, current will leak, supplying to earth.
That is like saying the current will leak along the wires.
It isn't a leak if you want it to happen.
If you have unbalanced loads, you need a neutral wire for the out-of-balance current to flow through

You can use the Earth instead.
Logged
Please disregard all previous signatures.
 

Offline theThinker (OP)

  • Sr. Member
  • ****
  • 106
  • Activity:
    0%
  • Thanked: 1 times
    • View Profile
Re: Does the primary winding of a power substation step down transformer need ground
« Reply #8 on: 15/12/2021 09:32:20 »
Quote from: Bored chemist on 15/12/2021 08:42:26
Quote from: theThinker on 15/12/2021 04:38:25
When the generator runs, current will leak, supplying to earth.
That is like saying the current will leak along the wires.
It isn't a leak if you want it to happen.
If you have unbalanced loads, you need a neutral wire for the out-of-balance current to flow through

You can use the Earth instead.
Thanks. I think I got it now. It is AC,not DC circuit.

I think the neutral of Y for transformer/generator could be earthed - or should be earthed.
Logged
 



Online evan_au

  • Global Moderator
  • Naked Science Forum GOD!
  • ********
  • 10237
  • Activity:
    37%
  • Thanked: 1227 times
    • View Profile
Re: Does the primary winding of a power substation step down transformer need ground
« Reply #9 on: 15/12/2021 20:13:01 »
3-phase AC electricity was invented by Nikola Tesla, and it is still the dominant form of delivery around the world.

There are two main ways of organising 3-phase electricity delivery:
- "Y" or "Star": This has a central point, which is usually earthed. Star connection is usually used for domestic distribution, as the earth gives additional safety in case of accidental human contact.
- "Δ" or "Delta": This has no central point. It is more often used at higher voltages, and in long distance transmission. In these cases, Delta is not earthed, as it would require bigger insulators on the other two phases, and would cause unbalanced currents in the 3 phases*. It normally connects to a Star at the other end of the high-voltage line, which is earthed

*If you watch the arrangement of the 3 wires on long distance transmission lines, you will see that over several kilometers, they rotate the 3 wires, so that each phase has a turn being closest to the physical ground, and hence an equal capacitance to ground. [Do not try this if you are the driver!]

Most countries with 220-240V AC distribution put a distribution transformer in the street, serving many houses.
The USA and Canada, because of their lower distribution voltage (110V AC) suffer from higher resistance losses, so they  usually put a step-down transformer outside each couple of houses, producing 2 phases of 110V (earthed) + 220V (not earthed).

See: https://en.wikipedia.org/wiki/Delta-wye_transformer
Logged
 



  • Print
Pages: [1]   Go Up
« previous next »
Tags: transformer  / electricity  / power transmission 
 

Similar topics (5)

Is Boron power "Fission" or "Fusion"?

Started by evan_auBoard Physics, Astronomy & Cosmology

Replies: 6
Views: 6505
Last post 08/02/2016 22:47:48
by alancalverd
Can matter and anti-matter annhilation one day power the earth?

Started by spook1456Board Physics, Astronomy & Cosmology

Replies: 1
Views: 9285
Last post 11/04/2011 17:46:33
by JMLCarter
Would a flail-type wood chipper use less power if chipping frozen wood?

Started by peppercornBoard Technology

Replies: 3
Views: 9770
Last post 21/04/2018 10:58:02
by chris
Can water shortage, power shortage, & nuclear waste be simultaneously fixed?

Started by Atomic-SBoard The Environment

Replies: 4
Views: 7133
Last post 11/06/2018 06:16:38
by pradeepkumar
Is 'power fantasy' a cultural thing or a deep-rooted male thing?

Started by ConfusedHermitBoard Physiology & Medicine

Replies: 6
Views: 6318
Last post 05/09/2012 04:41:19
by CliffordK
There was an error while thanking
Thanking...
  • SMF 2.0.15 | SMF © 2017, Simple Machines
    Privacy Policy
    SMFAds for Free Forums
  • Naked Science Forum ©

Page created in 0.1 seconds with 53 queries.

  • Podcasts
  • Articles
  • Get Naked
  • About
  • Contact us
  • Advertise
  • Privacy Policy
  • Subscribe to newsletter
  • We love feedback

Follow us

cambridge_logo_footer.png

©The Naked Scientists® 2000–2017 | The Naked Scientists® and Naked Science® are registered trademarks created by Dr Chris Smith. Information presented on this website is the opinion of the individual contributors and does not reflect the general views of the administrators, editors, moderators, sponsors, Cambridge University or the public at large.