Some related questions:1) Assume the power station generator is Y connected. Can the neutral point be earthed? ( I think it would be a "fault" condition).
2) Assume we take out the iron core in the step-up transformer - 30kV to 300kV. If we try to run the system with this air core, what will happen?
Can the neutral point be earthed?
If we try to run the system with this air core, what will happen?
Quote from: theThinker on 14/12/2021 15:44:51Some related questions:1) Assume the power station generator is Y connected. Can the neutral point be earthed? ( I think it would be a "fault" condition). It's not a fault, an earthed system needs to be star connected so that the star point provides a common earth for all phases. In a delta system you'd have to earth one of the lines, in which case you'd end up with one phase live at both ends.Quote2) Assume we take out the iron core in the step-up transformer - 30kV to 300kV. If we try to run the system with this air core, what will happen?The magnetising current will go though the roof because you've lost most of your inductance, and the leakage inductance will go up because you're losing a lot of your coupling.
When the generator runs, current will leak, supplying to earth.
Quote from: theThinker on 15/12/2021 04:38:25When the generator runs, current will leak, supplying to earth.That is like saying the current will leak along the wires.It isn't a leak if you want it to happen.If you have unbalanced loads, you need a neutral wire for the out-of-balance current to flow throughYou can use the Earth instead.