I would like to know if it would be possible to run Cold water through your central heating system? Doing so would cool the air around the radiator. If you connected a fan/vent system to either move the hot air from above to the radiator or just found a way to move the air around the room; the effect should work to reduce the overall temperature in the room.I don't know how effectively you could regulate the temperature. It certainly would be a less environmentally damaging way of cooling a building, if for no other reason than, it might be possible just to add a few componets to existing central heating systems. You certainly would not have hot air thrown out of the building as you do now with air conditioners.There may be problems with the changing temperatures and the pipe work, and the cooling process may be slightly slower than air con, but it would be cheep and easy(hopefully).So would it work?
I think he's asking if cold water could be pumped through central heating radiators to produce a cooling effect, as opposed to hot water warming the room.
Is that not what a swamp cooler does ? Is that different?
Doesn't it blow air through a water like saturated filter or panel so when water evaporates from panels you get cool moist air right??? that
Here they set up or hang from your ceilng water is used to pump small amounts in! as above if I am right!
Quote from: Karen W. on 20/09/2007 12:54:13Doesn't it blow air through a water like saturated filter or panel so when water evaporates from panels you get cool moist air right??? that Quote from: Karen W. on 20/09/2007 12:55:30Here they set up or hang from your ceilng water is used to pump small amounts in! as above if I am right! You mean an Emerson cooler they suck air through a wet filter. No totally different, didn't know they were called swamp coolers in the states though, so I learnt something new today; Thankyou karen.
Quote from: sooyeah on 20/09/2007 13:06:28Quote from: Karen W. on 20/09/2007 12:54:13Doesn't it blow air through a water like saturated filter or panel so when water evaporates from panels you get cool moist air right??? that Quote from: Karen W. on 20/09/2007 12:55:30Here they set up or hang from your ceilng water is used to pump small amounts in! as above if I am right! You mean an Emerson cooler they suck air through a wet filter. No totally different, didn't know they were called swamp coolers in the states though, so I learnt something new today; Thankyou karen.Your welcome I know very little about them.. the exact process I am not sure of someone more qualified then me could probably explain properly.. I am probably wrong anyway.
The main problem when using a central heating system for cooling is that radiators are designed to radiate heat. They can do so because their temperature is higher than the surroundings, so they emit a net heat radiation.If you run cold water through your central heating system, the radiators will absorb heat radiation from the surroundings, but these surrounding are not designed to radiate.
You will have some cooling of the air between the panels of the radiator, which will make that air heavier and create a circulation, but for a same absolute temperature difference between radiator and surroundings, the yield (= heat transfer) will be lower.
A second point is that because of the cooling of the air, you will have condensation of water on radiator panels. Airco installations are designed to deal with this, a central heating system is not, and you'll have your radiators dripping.
Besides, this condensation gives off energy (heat) and will again reduce the effectively of your cooling system.
plus there's the cost of keeping the water cold enough to make any difference. water heats up pretty quickly
Eric are you saying that it would effectively remove water from the air as well?
Just for the record radiators don't do a lot of radiating. Almost all the heat transfer is by convection.
You could run cold water through the same pipes and radiators and get an effect. There are 2 problems what do you do with the water fater it warms up (or equivalently, how do you cool it back down again)
and 2 the heat transfer from radiators is typically from a radiator at about 60C to a room at about 20 so there's a 40 degree difference. With a "cold" radiator you would need to chill the radiators below freezing to get the same rate of heat transfer.
There's another problem too. If the radiators were cool enough, water would condense out onto them and drip off causeing damage to carpets etc and corrosion of the pipes etc.
Hi Sooyeah. What you're describing sounds like a water source heatpump, I think. Here are a few links that describe them.
http://www.eere.energy.gov/consumer/your_home/space_heating_cooling/index.cfm/mytopic=12640
http://www.toolbase.org/Technology-Inventory/HVAC/water-cooled-evaporative-air-conditioning