About 15years ago I was running a 1000kva diesel powered alternator at 60% load, in parallel with the grid, when the excitation failed. Not much happened other than the current shot up but not to dangerous levels and the pf went into a lead. The conventional wisdom is that such a scenario can lead to pole slip( ie desynchronisation ) with potentially severe consequences for the rotating diodes or worse to the coupler and/or the crankshaft. This was a brushless four pole salient pole 1500rpm lv machine. My question is this: with the massive damper fitted to all similar alternators that I have seen would the alternator not default to asynchronous operation wherein the damper would be analogous to a squirrel cage rotor, in the case of excitation failure?