In Europe, the standard tests for ground source heat pump units use 35 °C (95 °F) for T H and 0 °C (32 °F) for T C. According to the above formula, the maximum achievable COP would be 8.8. Test results of the best systems are around 4.5. When measuring installed units over a whole season and accounting for the energy needed to pump water through the piping systems, seasonal COP's are around 3.5 or less. This indicates room for improvement.
What sorts of devices, operating under what sorts of conditions are you referring to? Are these domestic systems, for instance?
Maintaining an indoor temperature of 293K against an average outdoor temperature of 283K, the theoretical limit or a UK domestic aircon or underfloor system is about 29, but most systems maintain the underfloor water temperature at 313 and a hot water tank at 333, plus losses in the water circulating pump and occasional weeks at outdoor temperatures below freezing, so however good the primary heat pump may be, an overall annual CoP above 3 is pretty good.
If there's no planning restriction, you can position a domestic air source pump at any height. Window or first floor level is usually convenient so no problem with it getting choked with leaves or recirculating chilled air.Ground source must become less efficient with time as the immediate ground cools, so you need an oversize collecting coil at these latitudes.
Apart from environmental benefits a COP of 3 would not be of any benefit to me as a Joule from electricity costs me more than three times that of one from burning natural gas.If there is cheap electricity available from Hydro or Plutonium producing plants it would be a help to me but not in the UK
Yes. Strongly recommended for a new build or major refurbishment!